On some of our larger and more critical units, we install an "Active Leak Detection" scheme. It's the Xfmr Low (Alarm) contacts along with a pressure transducer installed in the lower manifold, via an overbuilt PLC that converts the pressure to a contact. When both signals are sent to the Xfmr relay in the house. If both signals are high for a defined time(relay logic)-TRIP 86T, target Active Leak. If we get Low-Low and Pressure, the relay logic trips immediately.
I believe the scheme was developed by one of the Transformer Monitoring vendors. There seems to be a lot of unnecessary vendor related PLC hardware in the cabinet for what it does, but this is what is used. It's factory installed on new units, and retrofitted on older ones.