The dead times you chose can be affected by the upstream protection. If the upstream device is an electromechanical relay, you have to be concerned with the disk travel of the relay. Increasing the dead times can improve coordination. Some typical times shown in the Cooper manual on distribution protection are
Inst, 2.0, 2.0
2.0, 2.0, 2.0
2.0, 2.0, 15.0