I am analyzing the grounding of a 911 center served from a 12 kV distribution line. I have calculated the Ground Potential Rise (GPR) of the ground system for a 12 kV fault at the transformer pole serving the center. I am using SES MALT and FCDIST software. MALT calculates the ground resistance and surface potentials. FCDIST determines how much of the fault flows back to the substation through the earth and how much flows through the neutral.
The GPR at the center is high, but not unreasonable, about 1460V. I decided to see what would happen at the 911 center if there were a fault on the transmission side of the 100-12kV substation serving the 911 center line. I didn't expect this to be a governing factor, but it turns out that the GPR at distribution line pole grounds and at the 911 center are almost as high as the substation GPR, over 11 kV.
This is essentially a transferred potential problem, with the distribution neutral propogating the substation GPR to all of the distribution pole grounds, with little attenuation.
If the GPR is this high at a distribution pole where there is no ground grid, just a single rod, the touch voltage would be dangerously high. We use IEEE Std 80 and go to great lengths to reduce touch voltages inside substations to safe levels. There are no standards in the US that I know of for touch voltages at distribution poles. Does anyone know of any studies made of this situation or practices to alleviate the problem?
The GPR at the center is high, but not unreasonable, about 1460V. I decided to see what would happen at the 911 center if there were a fault on the transmission side of the 100-12kV substation serving the 911 center line. I didn't expect this to be a governing factor, but it turns out that the GPR at distribution line pole grounds and at the 911 center are almost as high as the substation GPR, over 11 kV.
![[shocked] [shocked] [shocked]](/data/assets/smilies/shocked.gif)
If the GPR is this high at a distribution pole where there is no ground grid, just a single rod, the touch voltage would be dangerously high. We use IEEE Std 80 and go to great lengths to reduce touch voltages inside substations to safe levels. There are no standards in the US that I know of for touch voltages at distribution poles. Does anyone know of any studies made of this situation or practices to alleviate the problem?