Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Distance for Analog Signal Transmission

Status
Not open for further replies.

Pyland

Mechanical
Nov 6, 2002
1
Question came up as to what distance can a 4-20 mA analog signal from a transmitter can be run if terminating to a card on a DCS or PLC.

 
Replies continue below

Recommended for you

Depends on if there is enough voltage available to overcome the resistance (wire length and resistance of DCS, etc).
 
buzzp is right. Say a transmitter will accept a 500 ohm max load. If you drop the signal across a 250 ohm resistor (creating a 1-5 VDC internal signal), that leaves you with 250 ohms to work with. If 18 ga. copper wire was the only resistance, you could install the transmitter over 3 miles away!

However, intermediate connections, bends in the wire, internal resistance (control system and transmitter), power supply, etc. all contribute to resistance.

A more practical max distance is 1 mile, and that's only under ideal circumstances.
 
Status
Not open for further replies.

Part and Inventory Search