Part 6 of BS7671, Requirements for Electrical Installations states:-
Section 601,
Part 601-04-01
Except for SELV (Safety Extra Low Voltage) for a circuit supplying equipment in a room containing a fixed bath or shower where the equipment is similarly accessible with exposed conductive parts of other equipment or with extraneous conductive parts, the characteristics of the protective devices and the earthing arrangements shall be such that, in the event of a fault to earth, disconnection occurs within 0.4 secs.
You need to read the whole of Section 601 because it talks about equipotential bonding and lots of other things.
Regards