@ Mr bacon4life (Electrical)22 Feb 23 01:05
"....#1. Where is your project located? This forum has folks from all over the world. #2. At around 1000 volts there are new kinds of considerations for the design of electrical equipment. For example, at 600 volts a power cable consists of just a conductor surrounded by insulation. Above 1000 volts, there is an additional..."
1. In Europe where IEC is the norm, LV covers up to 1000V ac and 1500V dc. All equipments up to 1000V ac and 1500V dc are considered as LV; covered by the same standard (e.g. IEC 60947-x ...) for breakers, contactors, disconnectors etc...
1.1 Note: In most cases a 1000V ac Breaker /disconnector is actually the same 690V ac breaker/disconnector but labelled with lower Icu , ics, Icw etc.... Therefore physically interchangeable. Attention: But with lower ratings.
2. IEC 60947-x covers up to 1000V ac and 1500V dc. Therefore, Breakers, Disconnectors, Contactors etc... are covered by this single IEC standard.
Che Kuan Yau (Singapore)