Hi wstokes,
I’m chiming in late and they were good posts above, but it sounds like you were left with a question so I wanted to add detail:
The AHU cooling coils should discharge cold air, ~46-48°F, when the outdoor dew point is above 44.6°F (the desired dew point of the room). The reheat should then cycle to maintain space temperature, or to temper the discharge air to a higher value—depending on the attached system.
The humidifier should be disabled during dehumidification when the cooling coil removes moisture (any time the outdoor air dew point is above 44.6°F).
If the supply duct high limit humidity sensors were better, they wouldn’t likely be pegged. Real relative humidity typically drops into the low 90s with cooling coil bypass factor. Cooling coils with more fins per inch and/or more rows might have lower bypass factors (on the order of 10%). Coils with less fins per inch and/or less depth will have higher bypass factors (15-25%). The bypass factor reduces leaving dew point below the dry bulb temperature. Greater bypass means lower dew point for a given dry bulb temperature. The leaving air should therefore be less than 100% RH unless there is a 0% bypass factor. Some sensors fail however, pegging high if the humidity approaches 95% or if any water droplets form on the sensor.
During winter the reheat coil and the chilled water should not be used and should be disabled. The discharge air temperature of the AHUs should be raised and then the high limit humidity sensors (assuming they’re placed right, downstream of the humidifiers) will function as intended.
Consider modifying the program for the AHUs to do the following. This assumes an AHU serves the space directly with no additional terminal boxes with reheat:
Above 45°F OA dew point temp:
• Disable heating and humidification.
• Enable chilled water and reheat.
• Set cooling coil leaving air temperature to 47°F.
• Modulate reheat to maintain space temperature.
Below 45°F OA dew point temp and above 45°F dry bulb:
• Enable humidification to maintain a 40% exhaust
relativehumidity with a discharge air high limit of 85%
RH.
• Disable reheat.
• Use AHU heating and chilled water, without overlap, to
control the discharge air temperature setpoint on a reset
schedule that maintains the room temperature setpoint.
For example, a 68°F room may cause a 75°F discharge
setpoint, a 72°F room yields a 55°F discharge setpoint.
Below 45°F OA dry bulb temperature:
• Maintain humidification control.
• Disable chilled water and reheat.
• Use AHU heating only to maintain the discharge
temperature reset schedule based on room temperature.
Sorry – I meant for this post to be shorter.