khadisa:
You still do not supply much info.
From the kind of relay you are using I suppose it is an old installation. How long do you experience this fault? Is it a recent fault?
Combined REF and differential schemes are not unusual. If the scheme is stable on load currents, but unstable on through-fault currents, I would still suspect a wrong CT - most probably a CT that saturates under heavy current conditions. Also remember that these CTs have to be class X CTs. I would not suspect a reversed CT, because then your scheme would be unstable under normal load conditions.
Number of factors that need consideration for a differential scheme on two winding transformer:
a) Transformer vector group (phase shift between HV and LV)
b) Mismatch of HV and LV CTs
c) Varying currents due to on-Load Tap changer (OLTC)
d) Magnetizing in-rush currents (from one side only)
e) Possibility of zero-sequence current de-stabelizing the differential for an external earth fault.
Factor (a) need no consideration, because there is no phase shift between HV and LV. (Transformer Y/y)
[red]Can you confirm that your main HV and LV-CTs are connected both in star? Interposing CTs (both star/delta) seems to be fine.[/red]
The delta connection of the interposing CTs provides a path for circulating zero-sequence current, thereby stabilizing the protection for an external earth fault as required by factor (e)
[red]Seems to be fine[/red]
As the magnetic inrush is predominately 2nd harmonic, filters are then utilized to stabelise the protection for this condition (d)
[red]No inrush trips, seems to be fine[/red]
It is necessary to bias the relay to overcome current unbalances caused by (b) mismatch of CTs and (c) OLTC. The desired setting is dictated by the operating range of the OLTC which is responsible for the biggest current unbalance under healthy conditions.
[red] Seems to be fine because transformer operate under full-load conditions[/red]
[red]Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon[/red]
Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376