different currents on the parallel wires of a phase 2
gaux
48
hi, all i got a question that maybe is very easy for electric guys, we have a generator, 400 V 1500 A, and we use 6 wires to get out the current, and i got diferents currents on each wire, i tight them again but it´s not sucesful, and now i don´t know why...we cheek the terminals and all seems to be ok, does somebody know why...
the diference is about 10 % of the current....?
i hope somebody could help me cause i´m worried about some wire will burn.... thanks in advance
10% difference might not be worth worrying about. But if you can get your hands on a thermograph, take a quick look at the cable terminations while under load just to make sure that a higher impedance of one of the paralleled conductors isn't due to a bad crimp or tightening torque.
Good point, PHovnanian!
The first thing I would do on cases like these is to verify good joints. Small contact resistances on any cable termination means a lot, and could explain why current sharing variations are pronuonced.
Is the motor paralles wound? E.g.: Does the motor have six separate windings?
Are the motor windings in Wye (Star) or in Delta?
Tx.
Regards . . .
Jim S. Nasby