- Jun 24, 2017
- 194
Hi Friends,
I have a site that is in process of getting upgraded with addition of 300kW diesel generator. The MCC is a 480V, with no single phase loads, although the utility feed is a 4 wire with neutral wire landing on neutral bar inside the MCC. Would it be a bad idea to bring 3 phase wires and ground from genset to MCC? I'm thinking that if in the future the owner adds a 277V single phase load to the system, the standby power source would not be able to accommodate it.
Thoughts?
EE
I have a site that is in process of getting upgraded with addition of 300kW diesel generator. The MCC is a 480V, with no single phase loads, although the utility feed is a 4 wire with neutral wire landing on neutral bar inside the MCC. Would it be a bad idea to bring 3 phase wires and ground from genset to MCC? I'm thinking that if in the future the owner adds a 277V single phase load to the system, the standby power source would not be able to accommodate it.