DH-485 Comms between AB 5/02 and 5/03

Status
Not open for further replies.

Electromechanical30

Industrial
Sep 15, 2004
45
I was wondering if there is a quick and painless way to add another SLC 4 slot rack that's running a 5/02 CPU to my existing SLC 4 slot rack running a 5/03...

The existing 5/03 talks VB script running on a PC via the serial port. I have an 2 8 input triac cards and a 8 output triac card in this system.

Recently, I have acquired another rack with a 5/02 CPU, 2 16 DI, and a 16 DO card. I'd like to integrate the two systems.

I did visit AB's homepage. Their DH-485 overview states that a network interface adapter would be needed.

Finally my question is: Can I connect the two CPUs using the DH-485 ports and configure the programs accordingly?
Any insight and reference is greatly appreciated!!
 
Replies continue below

Recommended for you

How about using an interconnect cable between the racks. You will not need a second CPU. I have two 13 slot racks tied together this way. Up to 3 racks can be tied together.
 
I will look into this option.
I figured that since I had the two racks with CPU cards, I'd try to integrate the two, if it were as easy is plugging in a patch cable to both DH485 ports and changing some code in my programs...

Thanks for the tip!
J
 
If your rack are within 3ft of each other (same cabinet in other words) Then the chassis interconnect cable it the way to go. From a programming standpoint it appears to be one local rack.

You might do some homework on DH-485 networks. The only time I have used it is with a SLC 5/03. I used DH 485 to communicate to a TCP flatpanel. I am sure AB mades a cable, or give pinoust so you can make your own. You would then need to write some message instructions to handle interlocks between the 2 processors.
 
To connect the racks together with a processor in each rack, you will need to set up a DH485 network. A (1747-AIC or 1747-NET-AIC) Isolated Link Coupler is needed at each processor or node. They are connected together with twisted pair. AB sets the distance at 4000ft and a max baud rate 19.2K.

Steve
 