And not all interlocks are the same. A few years ago I was commissioning the protection on a 500kV 3 breaker ring bus. Each breaker disconnect was a combination Disconnect Switch / Ground Switch (DS/GS). The DS/GS had a mechanical interlock. I looked into the controls and noticed that it was only a mechanical interlock. I asked the questions about the lack of electrical interlock between the motor operated DS & GS. I was told it was not necessary.
The crew setting up and testing these switches inadvertently found a way to electrically operate the switch while interlocked and destroyed the mechanical interlock. Shortly thereafter, we were designing and installing an electrical interlock for the switches. Fortunately this was all during commissioning and no real harm was caused.
I just finished up commissioning a 5 bay GIS ring. All switches, ground switches and breakers were electrically interlocked. The switches themselves had mechanical interlocks that would not allow manual operation of the devices without the electrical interlocking being satisfied. For these types of systems, with all of the switches and grounding switches being motor operated, I believe it is imperative to have said interlocks installed. In this case, only the breakers had SCADA control.
I believe if it's motor operated and certainly if it can be operated remotely, an interlock system should be installed. In an AIS station with mostly manually operated switches, in a utility environment, this is not always done. A lot of utilities don't utilize ground switches and rely on hanging grounds, after checking for lack of potential.