We call such rebar and anchor bolts "decoration." If I had to think of a technical way of doing it though, I'd get the compression forces based on strain compatibility and reduce the compression development length using the ratio As/Asreq.
I think 0.5% is the provision is for "compression members with a cross section larger than required by considerations of loading" per ACI 318-08 10.8.4, it lets you reduce it by half. So half of 1% is 0.5%. A pedestal can be taken as the size of the column above it in the ACI 318 section about footings so theoretically, we can go way lower than 0.5% by considering only the area with column above and pour a ton of concrete around it.