JoshPlumSE
This is really more of a question about RISAFoot rather than RISA-3D. But, since there isn't a forum for that program I thought I would post it here.
For years RISAFoot has reported the required straight development length for the pedestal bars compared to the available development length based on the thickness of the footing.
For tension these bars are typically hooked and will, therefore, have enough development length. For compression, however, the thickness of the footing limits how much available development length there is. The result is a failed development check in most cases.
Some comments / questions:
1) The most popular footing design example we have is in the PCA notes. This is the section where they require the full development length for bars in compression. They even imply that the designer needs to increase the thickness of the footing if this development length isn't met.
2) Their rationale for this is ACI code section 12.5.5 which says, "Hooks shall not be considered effective in developing bars in compression.".
3) What's not said in this example is WHY you need to develop these bars in compression. What type of failure are we going to see in these hooked bars if they are not developed in compression? For compression, I would personally be more worried about concrete bearing failure, soil failure or punching shear.
Is anyone out there actually using this compression development length as a requirement? Talking myself through this, I'm guessing that folks are really using the 12.2.5 reduction "based on excess reinforcment" to reduce the required development length?
This is something that has always bothered me about the program. It just never agreed with my past design experience. Therefore, I thought that this forum might be a good place to broach the subject. Any suggestions or insight about the PROPER way to develop these bars would be appreciated.