According to ACI 318-14 Section 25.4.2.3, the development length of a bar can be reduced when considering the confining effects of transverse reinforcement. Does the code require this transverse reinforcement to be fully developed on both sides of the potential splitting plane?
The commentary discusses the removal of the transverse steel's yield strength from previous versions of the equation, as "tests demonstrate that transverse reinforcement rarely yields during a bond failure". This would imply that the transverse steel does not need to be fully developed, as it does not need to reach its full yield strength to be effective. But common sense says that it must have some embedment length or hook to provide some nominal amount of clamping force.
If it does need to be developed, can you reduce the length using the As,reqd/As,provided ratio? If so, is that based on the main bar's utilization or the transverse bar's? If the latter, how would you quantify that?
The commentary discusses the removal of the transverse steel's yield strength from previous versions of the equation, as "tests demonstrate that transverse reinforcement rarely yields during a bond failure". This would imply that the transverse steel does not need to be fully developed, as it does not need to reach its full yield strength to be effective. But common sense says that it must have some embedment length or hook to provide some nominal amount of clamping force.