Easy, look for NFPA 850 (recommended practice).
Basically it says:
- 500gpm for 2 hrs plus the design scenario systems demand (i.e fixed or mobile systems like sprinklers, deluge systems, foam equipment, monitors, etc. involved in a reasonable design fire scenario with simultaneous water demand with their respective design duration).
- The 850 does not tell if the mobile equipment should be included or not in the 500gpms
- This will give a design water flow and a water reserve volume. The water reserve design volume should be replenished on 8 hrs or less.
If possible consider more water for long fire combat operations, cooling or after fire washing up.