You can determine the instantaneous trip setting of your MCCB if you know the full load current/rated current of your individual or total loads. Assuming, after having performed your calculation and considered the inrush current, safety factors, etc…and come out with a 220 amperes current of your static load, the 220 amperes is NOT the instantaneous trip setting of your MCCB.
To protect your static load you have to select your MCCB setting from NEC article 240, sub-section 240.6.(A), the instantaneous trip setting of your MCCB as per NEC should be 225A. Next, you have to select your MCCB ampere frame size as well from the catalogue of MCCB manufacturer, either select a 225AF/225AT or 250AF/225AT.
Check also the sub-sections 240.6.(B) & 240.6.(C) of the NEC.