The local agency having jurisdiction will set the minimum requirements for sewer design. The requirement for a minimum velocity in the sewer to prevent solids deposition calculates into a minimum design slope requirement.
Whether you are expressing the sewer design criteria as the minimum velocity in terms of ft/sec or in slope of the sewer, you are essentially setting the same minimum design criteria.
Here are a few examples:
Gravity sewers shall be designed for a minimum velocity of three fps that exists at the time the pipe is placed into service. City Engineer approval must be obtained to use lower design velocities, except in the extreme upper reaches of the system with few connections. In these cases, 8-inch diameter minimum pipe size and 0.0044 ft/ft minimum slope will govern except for the last upstream reach to a terminal maintenance hole where 0.0060 ft/ft minimum slope will govern.
Sewer Pipe Design • Sewer pipes shall be designed for minimum velocity of 2 feet per second.
• The minimum pipe size for sanitary sewer is 8” inside diameter.
• If a flatter slope is proposed, the pipe shall be designed to prevent settlement of solids in the pipe.
3. Slope -
a. All sewers shall be so designed and constructed to give mean velocities, when flowing full, of not less than 2.0 feet per second, based on Manning's formula using an "n" value of 0.013. Based on an "n" value of 0.013, the following are the minimum slopes which should be provided; however, slopes greater than these are desirable:
Sewer Minimum Slope
Ft/100 feet
4 inch 1.05
6 inch 0.60
8 inch 0.40
10 inch 0.28
12 inch 0.22
14 inch 0.17
15 inch 0.15
16 inch 0.14
18 inch 0.12
21 inch 0.10
24 inch 0.08
27 inch 0.067
30 inch 0.058
36 inch 0.046