I've operated systems like this and designed them for people all over the world. There are two key learnings:
[ol 1]
[li]At these pressures, none of the empirical gas flow equations (i.e., AGA Fully Turbulent, Panhandle A, Weymouth, etc) come close to matching real flows. Their assumptions preclude their use in these conditions. The Isothermal Gas Flow equation still does pretty good, but you absolutely have to iterate each step until the Reynolds Number that went into the friction calc is within about 5% of the Reynolds Number of the computed flow. Fail to do this and your dP will be off by 50-100%. Transient models at these pressures are far worse than worthless--the flow will change flow regime on a milisecond time scale and the transient models are working on a minute time scale.[/li]
[li]EVERY SINGLE LINE MUST BE PIGGABLE. No exceptions. For flow lines from wells to trunks install
Argus Pigging Valves (watch the video at the bottom of the link, the valves are pretty cool and only cost about 20% more than trunnion ball valves). Put in piggabale drips (I've got a design on my web page that you can have for free). With all this equipment you have to use it. My Pumpers watched the line pressure on their wells very closely and when the variability increased slightly they ran flow line pigs. Watch your system dP's. I recalibrated my pipeline model quarterly and flow lines that needed a lower efficiency to calibrate than they needed in the last calibration got their pigging schedule increased. Lines that showed an improved efficiency two quarters in a row got their frequency decreased. The pigging schedule ruled our lives since we treated the gathering system as our primary tool of reservoir management.[/li]
[/ol]
A line that looked like it was going to be properly sized (Using the Iso equation) at 50 psig wellhead pressure is probably still going to be fine at 40 psig wellhead pressure. If you are using another correlation then it will certainly tell you to go to bigger pipe. You probably should resist that.
David Simpson, PE
MuleShoe Engineering