Gentlemen,
Pls forgive how late I am to this thread, but I am new to this forum and the issue you previously discussed is very similar to a dilemna I have. Here is my situation:
We are designing a fire station for Creech AFB, NV. We also have to follow requirements of UFC 3-600-01, which states the design area must be at least 3,000 ft2. Since the remote area is a vehicle bay (2,978.88 ft2/ordinary group 1/ceiling 25 ft at the peak) and the roof is sloped more than 2 in 12 (add 30%), my minimum design area is 3,900 ft2, which goes well beyond the boundaries of the vehicle bay. On the other side of the fire-rated wall is the admin area, common areas, and sleep rooms, etc. (all light hazard).
Question #1: Since the remote area falls short of the 3,900 ft2 total I need, am I correct if I extend the design area into the light hazard area, even though the vehicle bay is separated from the light hazard areas by a 2-hour wall? I believe I am correct, but want to be sure.
I realize that the vehicle bay is 900+ ft2 short of the 3,900 ft2 requirement, but I think my dilemna comes from my belief that if a fire were to develop in the vehicle bay area, the sprinklers should be able to control the fire before it gets through the wall into the light hazard area. Designing the system for a 3,900 ft2 area at 0.15 gpm per ft2 will require what I call a significant water supply. And although the UFC doesn't allow the room design method, this seems to be a perfect situation for an approved deviation/exemption from the UFC requirement. My opinion, of course. I freely admit I may be waaaaaay off.
Question #2: should I recommend to my project engineer that we install a horizontal gypsum roof in the vehicle bay area? That would take the design area back to the 3,000 ft2 range and allow me to calculate just 1 extra sprinkler from the light hazard area, keeping the water supply requirements down. This is not my favorite option because of access to sprinklers for maintenance, but it is an option...maybe...if we put in access portals, which may open up a whole new can of worms that I won't go into on this post.
I've already calculated the vehicle bay (30 SSU sprinklers) and including the 250 gpm inside/outside hose requirement, I am looking at approx. 761 gpm so far. My fear is that if I have to add approx. another 11 sprinklers from the light hazard area, even at 0.1 gpm per ft2, that may push the water supply requirements "too high."
Sorry this was long winded. I am going to finish up the rest of the 3,900 ft2 design area to see where that takes me. I just wanted some guidance to sanity check any assumptions I may have made. Thanx in advance for any help you can provide.
Shawn Lee