@waross
Quick answer to your follow up post, we use plastic conduit from riser to ground, i thermal gun those and all seem well.
To your initial reply (which I extremely appreciate this knowledge as I also get to learn):
<terminology/reply clarification>:
-“time to roll the connection”?
-“3640amps on secondary”, per secondary phase or all 3 phases combined?
—————
This week (Thursday or Friday, due to weather), I’ll have utility come inspect cutout holder and fuse barrel etc… (excellent recommendation)!
Also to step back just a bit (if, time to roll the connections means put full load on and see what happens):
Then the only difference as of current moment that’s been done is a 200amp fuse in place of the previous 100amp, only on middle cutout not all of them. Each time we put on full load - cutout fuse blows in approx 1hr, twice now.
If roll the connections means set tap back to rated HV “A” 12470 @ 415/240v and see where the problem goes then our equipment might not run properly if it can’t step up to voltage.
(These questions/statement are my lack of knowledge, clearly not yours.)
I’m ready to test this transformer with troubleshooting in any direction because we’re going to have to replace it next week if it’s not cured, so just seeking clarification for a very motivated but novice person as myself.
I’ve followed other threads you’ve replied to and respect your input greatly, and appreciate angles of input from others as well.
(Even if we replace before resolve, I’m having xfrmr tested and sampled for root cause and will update this thread with whatever results come of it).