Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Delta Winding with grounding transformer on utility sub-transmission & distribution

rockman7892

Electrical
Apr 7, 2008
1,178
I've come across a few small municipal distribution systems recently that had either their sub-transmission or distribution systems served from and interconnection substation to local transmission system owned by others (larger IOU) and noticed that the low voltage side of these transformers for municipal sub-trans or distribution (IE 26kV or 12.47kV) was a delta winding with a grounding transformer.

I found this a bit odd as most of these transmission to distribution level transformers I've come across in the past have always had a wye winding. Would there be any particular reason for having a delta winding on the low side of a sub-transmision or distribution transformer? Only thing I could think of would be the presence of generation on sub-transmission or distribution?

Appreciate any insight from others who may be familiar with approach.
 
Replies continue below

Recommended for you

That would stabilize the incoming voltages.
That MAY allow a ride through of a primary loss of phase if the incoming was a wye configuration.
The downside of that is that it would back-feed full voltage into a lost primary phase.
 
Having a DELTA on the 26kV or 12.47kV distribution system is little odd because,
1) when that system is connected to a customer he will definitely have a DELTA winding in his 26kV or 12.47kV side. That means the distribution system will become a DELTA/ DELTA ungrounded system.
2) The distribution system has always to be effectively grounded to avoid over voltages during a ground fault and also from the safety point of view.
Looks like a ZZ transformer is already installed so that during phase to ground faults the COG is kept within at least 0.8 so that all phase to ground connected equipment such as surge arresters, VTs etc are operating within their limits.
 
In the areas that I am familiar with, there are seldom any 26kV or 12.47 connected customers.
Almost all customers are served by utility owned transformer connected line to neutral/ground and delivering 120/240V, 120/208V, 277/480V or 347/600.V
Hence the need for a neutral point by a grounding transformer or a wye connection.
 
How old are these installations?
I only ask because in my company a very similar situation is present, but it’s due to a change of system grounding philosophy over the last 100 years. The 55kV transmission system, which was the original system transmission voltage, was originally ungrounded. I’ve been able to confirm by pulling old drawings as far back as the 1920s that show the 55kV system delta connected with no ground reference. In the 1960s timeframe the company began to effectively ground the 55kV system by installing grounding banks.
Perhaps with these smaller utilities a similar change occurred.
 

Part and Inventory Search

Sponsor