I have come across this a few times now where an existing building is being given an addition which has a much higher roof. We plan to reinforce the existing 2x10 roof joists with LVL's as the drifting snow load is quite large. However, how does one assess the deflection accurately given that the E's are different? They are sistered side by side, would it be as simple as finding the weighted EsI for the combined shape?

In the past I have just sized the new reinforcing to take the entire deflection, which is way over-designed if deflection is what governs in my opinion, but it is quick.
 
Replies continue below

Recommended for you

what exactly did you model with sectionproperties?

The important part of what has been said is that if you look at them individually then it shouldn't be the same result as if you look at them as a composite.

I would expect the full composite behavior to be more favorable in terms of deflection. The reason why many people just look at them as fully non-composite beams is that the connection between the plys can be difficult to achieve the full composite.

If you put both sections into a section analysis software and include the difference in E in that analysis, it should provide a fully composite result based on the transformed section properties.



 
Here is an example:
Assumptions:
2.0E Weyerhaeuser for the LVL
Elvl = 2,000 ksi
Fblvl = 2.6 ksi
Ixxlvl = 115.42 in4

No.2 SPF 2x10
E210 = 1,400 ksi
Fb210 = 0.875 ksi
Ixx210 = 98.932 in4

Transformed Ixx, assuming Elvl as the basis:
Ixxcomposite = 184.672 in4
Ecomposite = 2,000 ksi
Capture_lmkg57.jpg


Deflection Formula for a simply supported uniform loaded beam:
delta = (5*w*L4*1728) / (384*E*I) = (22.5*w*L4) / (E*I)

EIcomposite = 369,344 k*in2
delta = 6.09188e-5 *w*L4

Load distributed based on member stiffness:
∑ EI = 369,344
EIlvl/∑ EI = 0.625
EI210/∑ EI = 0.375

deltalvl = 0.625*22.5*w*L4 / EIlvl = 6.09188e-5 *w*L4
delta210 = 0.375*22.5*w*L4 / EI210 = 6.09188e-5 *w*L4
 
driftLimiter said:
what exactly did you model with sectionproperties?

See screenshot below:

2x10:
E = 9500MPa
1-3/4"x9-1/4" 2.0E LVL:
E = 13789MPa

Screenshot_2023-02-21_144355_fnzy4q.png


1_syab5i.png


When I run the 5*w*l^4/384EI equation with the EI in the screenshot under the same loading as when I did the original approach to split the loading based on stiffness to match deflection, I get a much larger deflection when using the composite EI.
 