I have a question regarding composite steel framed floors. We have guidance in the code and AISC regarding individual member deflections, but I do not see anything about system deflections. Here’s what I mean:
Let’s say we have a composite floor on a 30’ x 30’ grid. If the beams and girders are both designed to meet L/360 for combined dead and live loads, each would be designed to allow 1” of deflection. Which sounds good initially….but if the beams are 10’ on center, the system deflects 2” at mid span of the middle beam (beam ends go down 1” with the girder, then at beam mid span, there is another 1” of deflection)
This seems too high.
How do you guys deal with this in design? What are your limits?
Let’s say we have a composite floor on a 30’ x 30’ grid. If the beams and girders are both designed to meet L/360 for combined dead and live loads, each would be designed to allow 1” of deflection. Which sounds good initially….but if the beams are 10’ on center, the system deflects 2” at mid span of the middle beam (beam ends go down 1” with the girder, then at beam mid span, there is another 1” of deflection)