hippo11
Structural
- Mar 21, 2003
- 161
I've read on the Brick Industry Association website that L/600 or 0.3" should be used to avoid cracking mortar.
My question is, what loading would you apply this limit to? Of course it depends on construction sequence...
But I've heard from one person that it should be for superimposed dead + live, but then from another person that it should be for live only, with the rationale that the brick mortar is still wet when the brick "sees" its self-weight and therefore won't crack from its self-weight...
My question is, what loading would you apply this limit to? Of course it depends on construction sequence...
But I've heard from one person that it should be for superimposed dead + live, but then from another person that it should be for live only, with the rationale that the brick mortar is still wet when the brick "sees" its self-weight and therefore won't crack from its self-weight...