Background ->
This is a temporary shoring installation situation. It is a square excavation sheeted and braced with walers. The walers have kicker/braces at each corner, basically 4 perimeter wales with corner braces, all welded. Due to the sheeting being slightly slanted the hole gets smaller as you go down. The contractor installing the bracing was pushing at the center of the waler and bent/curved the waler (due to the restraint at the corners). It has deflected 5" in the weak direction. The welds are not broken. Attached is a photo (remember the deflection is vertical not horizontal)
Is there a way to analyze or decide if the beam is acceptable or if it is acceptable if pushed back into place?
I've back calculated the stress due to the deflection assuming a curved shape similar to what a uniform load would produce and the stress is above the allowable. However I'm not sure this is an appropriate method. Any good suggestions for repair?
EIT
www.HowToEngineer.com
EIT