Safety/disconnect switch rated under 600 V is considered acceptable as visible isolation device if readily accessible and lockable.
NOTE: Excerpt from IEEE Std 1547.2, IEEE Std C2, OSHA & NEC:
"There has been an evolution from the term visible-break"
• For voltage applications above 600 V “visible break” is still often used to indicate an isolating means with adequate visible inspection of all contacts in the open position. However, draw-out circuit breakers are generally acceptable as complying with the visible-break criteria.
• NEC: “isolating means” = “clearly indicating” has basically replaced “visible break.”
• NESC: Rules 173C, visible break requirement for circuit energized above 25 kV could be worked as de-energized without grounding the circuit.