Deep epoxy embedment in foundation wall
bnickeson
87
I have a podium-style apartment building where some large cast-in hold down anchor rods were omitted from the top of the foundation wall (despite my huge note on the drawings saying not to forget these). The location that was omitted was, of course, the shear wall with the highest uplift load on the entire building. Approximately 35 kips ultimate, though that was using Exposure C and realistically we're probably B. So you can keep in mind there was some conservatism there.
In any event, the foundation is a 12" thick wall and about 12'-0" tall. The uplift anchor rods are 1 1/8" diameter ideally placed 3 1/4" from the outside face of wall to the center of the bar. I can increase this to around 4" or so if needed. I am trying to post-install a single #9 bar in epoxy with a deep embedment to use development theory to resist this uplift load. I have enough vertical #5 bars in the foundation wall to prevent any tension breakout as these bars are developed where they theoretically cross the breakout cone. Looking at ESR 3814 for Hilti RE-500 V3, Table 31 gives a development length of 32" for a #9 bar and I am thinking of using 36". Section 4.2.3 states for embedment greater than 20db, that required minimum edge clear distance is to be 1 9/16" which isn't much. My biggest concern is just the proximity of the bar to the outside face of the wall and I'm wondering if this "development" of the bar is still adequate or if some other failure mechanism - like side face splitting or bond - would lower the capacity. I talked to Hilti's engineering help desk and they weren't any help.
Does anyone have any further experience with this? Will a 36" embedment in the top of the foundation wall be adequate to develop the strength of the bar? I don't believe we really have any other potential solutions for this location other than cutting a section of the wall down and re-pouring, which isn't an option since the walls are already partially backfilled.
Thanks.
Our IBC allows alternative design methods. There are certainly areas where designers have been known to deviate from ACI 318. For example, the Pallieraki method can be used in lieu of the standard shear-friction provisions to justify shorter embedments when full development on either side of the interface cannot be achieved. I’m sure the other codes (Eurocode, Chinese code, etc.) differ at least slightly from ACI 318.
I guess I understand why the commentary addresses the anchor reinforcement to only practically apply to cast-in anchors: their examples all use hooked bars, hairpins, etc. with shallow embedment anchors and/or close to an edge (for shear) that require precise placement. With a deep embedment when you're within 6" of multiple vertical bars that are developed well above the termination of your embedment, I'm not sure that "practical" exception still applies.
For instance, using shear as an example, if I have a high shear load acting perpendicular to an edge 24" away where my breakout doesn't work and I have #3 straight bars at 4" o.c. in the top face of my concrete member, is that anchor reinforcement still adequate? Assuming I only need two or three bars to adequately resist the shear load, I can pretty safely assume that those bars, no matter their exact arrangement relative to my post-installed anchors, will cross the breakout plane fully developed. This can easily be checked by sketching out the condition, development lengths, and breakout cone. In that instance, I think ACI's commentary that anchor reinforcement only apply to cast-in anchors is inaccurate.