zebco,
Is there another way to drop the water? (i.e could you install a few sections of sewer and manholes to drop the flow 30').
I would have a few things that come to mind with a direct 30' drop.
1) As gbam and dicksewerrat have outlined, scour would be an issue at the botom of the structure. Especially if you require a 42" outlet. I'm not sure a 3' sump would be enough given the drop.
2) Maintenance access. A 30'drop would require (depending on design standards in your area), 1-2 safety platforms within the structure. I would assume that you would want access given the drop. With the flow that would be entering the structure, you would have to provide a safe access for maintenance staff to the bottom of the structure.
3) Custom Structure Design. The structure that you would be looking for would have to be structurally designed and likley not something that could be obtained via a catalouge. Groundwater pressure, soil pressure, internal forces, etc would come into play with a structure like this.
4) Outlet. There would be quite a bit of turbulence at the bottom of the structure, it may also be beneficial to look further at the 42" outlet for erosion and scour d/s.
Hope this helps.