majesus
Electrical
- Aug 16, 2007
- 262
We are designing a 480V solidly grounded system for an industrial mine located in the Southern USA, where the climate is mild and the area will be designed with a solid industrial ground grid with multiple ground rods. Customer has requested that all 480V branch circuit feeder (15A CB and higher) come with dedicated ground fault protection as they have had issues with intermittent ground fault. One example given was lighting transformer failure which caused a fire that could of been prevented by using dedicated ground fault protection.
I haven't seen any 480V solidly grounded system with ground fault detection unless the feeder was for mobile equipment or another application I've experience was way up north where throughout the year, the ground was frozen Tundra and with permafrost and frequent ice accumulation throughout site, grounding was difficult. We provided ground fault protection on all feeders for that site.
However, for this current mine application, the climate is mild and as mentioned, it is a solid grounded system in an industrial site that shall a robust heavy ground grid installation. My experience is that individual feeder ground protection is typically not done on LV solidly grounded system.
We shall implement ground protection for all the LV feeders as per the client's request, however I'm curious on feedback from other member's experience.
Regards,
Majesus
I haven't seen any 480V solidly grounded system with ground fault detection unless the feeder was for mobile equipment or another application I've experience was way up north where throughout the year, the ground was frozen Tundra and with permafrost and frequent ice accumulation throughout site, grounding was difficult. We provided ground fault protection on all feeders for that site.
However, for this current mine application, the climate is mild and as mentioned, it is a solid grounded system in an industrial site that shall a robust heavy ground grid installation. My experience is that individual feeder ground protection is typically not done on LV solidly grounded system.
We shall implement ground protection for all the LV feeders as per the client's request, however I'm curious on feedback from other member's experience.
Regards,
Majesus