electricpete said:
I have heard discussion of transformer inrush being affected by residual magnetism, but I never heard anyone mention that for motors. I don't think it applies to motors. I can make some guesses (rationalizations?) for why that may be so. In order of relevance from my uninformed opinion:
A - * The transformer may be deenergized suddenly and all current and flux stops rapidly. In contrast, when we deenergize a motor there remains a current in the rotor which decays away. This will certainly tend to de-magnetize the stator core, since the decaying rotor current will cause the stator to see a decaying flux of alternating polarity.
B – The relevant reactance for the motor during inrush is the leakage reactance. For rotor slot leakage reactance, the relevant flux loop encircles a bar... and so a portion of it must go thru air. Since the loop path includes air and iron, the air tends to dominate the reluctance, and the effects of change in iron effective permeability (such as due to remnant flux) have reduced importantce compared to a device like trnasformer where all relevant flux loop paths are completely in iron without going thru air.
C – There is heavy saturation during energization of unloaded transformer for various reasons.... including the fact that the transformer operates further into saturation and the leakage reactances are smaller and magnetiing reactances higher. Also it is the magnetizing branch which saturates in a transformer since no secondary current, but magnetizing branch in motor will not saturate as much because rotor flux tends to cancel stator flux. Finally when we look at L/R time constant of a transformer during energization it is very high (due to high L associated with magnetizing branch)... in contrast for motor it is shorter since we have lower L (the leakage branch rather than magnetizing). So a small remnant flux can contribute a DC effect which exacerbates the saturation phenomenon in a transformer... but saturation is not much of a problem to begin with during motor energization. Maybe others can explain more especially on the transformer side.
I have another item to add to the above list (call it D) which is probably the biggest factor.
D - Remnant or Residual magnetism Br is dramatically lower for gapped core like a motor than for continous core like a transformer.
Below is excerpt from Magnetism Fundamentals:
It shows a B vs H curve for iron piece on the left and for iron piece with series airgap on the right.
We could have guessed the shape of the graph on the right using our knowledge of series circuits... for electrical circuits the voltages add and for magnetic circuits the mmf's add. So we can arrive at the series curve by adding in the horizontal direciton the linear airgap curve to the iron B vs H curve.
What is the difference in the curves? saturation level is roughly the same, width of hysteresis loop is roughly the same (Hc).
What is dramatically different is Br. Assuming the piece was driven into saturation and switched off without magnetization, the Br for the non-gapped core is very close to saturation, the Br for the gapped core is tiny.
This factor (D) is probably the biggest reason why residual magnetism plays so much more role for transformer energization peak current than for motors (followed by item A).
There was related discussion here thread238-120074
Reactorman made this exact comment at the end of the thread but it never really hit home for me until I saw the figure.
=====================================
(2B)+(2B)' ?