So you've been supplying the original 90V-rated field at 138VDC for years and it was not blowing the 30-amp fuse, and now it's been re-wound and it's supplying 51 amps at the same(ish) 140VDC?
I'm thinking the original winding probably had a high-resistance bad spot in it "for years" and this led you to compensate "for years" by over-supplying it beyond rated voltage, until it blew, and now that the winding is correct, it now draws more current because it no longer has that bad spot in it.
Reduce your field voltage supply until the voltage is within ratings (90 VDC) and current is hopefully what it's supposed to be, and within the ratings of your fuses.
What happens?