I used to know this one.
The difference between a generator and a transformer.
In a generator the EMF is developed by a conductor moving in a magnetic field.
In a transformer the EMF is developed by the change in the strength of the flux.
The difference between relative motion and varying field strength is such that the relative maximum EMFs are developed at 90 electrical degrees to each other.
In a simple example, the null point of generator action will correspond to the maximum EMF point of transformer action.
And the reciprocal, the point of maximum developed EMF of generator action will correspond to the point of minimum developed EMF.
So maximum voltage as a generator corresponds to minimum voltage when excited by AC and acting as a transformer.
Null point or zero point?
Simple theory tells us that there will be a zero point.
Why can't we find it?
It is a point, and the commutator segments and brushes are not a point.
The zero point is most likely midway between two commutator segments. You cannot find it with the brushes.
You may be able to find it by attaching voltmeter leads directly to opposite commutator segments.
Or:
Construction details, either design or faulty construction or non uniform materials may result in an non uniform magnetic field.
The windings on the left may not be reaching zero at the exact same point as the windings on the right.
At the null point the brushes may be in contact with two commutator segments.
This may be responsible for a slight variation as the rotor is turned.
The fewer poles and commutator segments the greater this effect.
A large variation as the rotor is turned:
I have used the null point test successfully as an "In Situ" growler test.
Set up for a brush neutral test. Leave the brushes fixed. Turn the rotor.
Any shorted or open windings will show up as a large meter deflection.
Short circuits and why do we need compensating poles?
Current in the rotor will set up a magnetic field at right angles to the main field. This field is normally much less than the main field, but the result is that the direction of the flux through the rotor is deflected and with it the null point.
The greater the load, the more current, the stronger the resultant field and the greater the effect.
The result is more sparking to the point of arcing at the brushes.
Commutating poles or inter-poles develop a third flux field to counteract the reaction field and restore the null point to the proper position.
A short circuit will generate a magnetizing force much greater than the original field.
This is how an an Amplidyne works.
The brushes are shorted.
A small current through the field will develop a strong magnetic field at right angles to the original field.
As the rotor cuts this second field, a voltage is induced. A second set of brushes at 90 degrees will is used and this power may be used to power a small motor or to excite the field of a generator driving a much larger motor.
In one model that I remember, zero to plus or minus 2 Watts of power into the field will control 1500 Watts of output.
In a normal generator this effect will be limited by saturation.
Bill
--------------------
"Why not the best?"
Jimmy Carter