Damper activation requirments by the Fire Alarm Panel

Status
Not open for further replies.

LGENE

Electrical
Joined
Jul 2, 2004
Messages
41
Location
US
Where can I find specific requirements for when Fire Alarm Panels need to tie to the Dampers? Thank you.

NFPA 90A and NFPA 72 (2002) 5.14.3.4
 
Depends on the application.

In the UK, smoke dampers in hospital theatres are deliberately NOT linked to the fire alarm system due to the danger of stopping the hygienic flow of purified air. The dampers in this case are manually operated by the fire brigade.

What application do you have in mind?

Friar Tuck of Sherwood
 