In an attempt to create a box section, AASHTO Category E, with a required CJP at all locations due to large tensile stresses and stress reversals, we have run into a constructability issue. On another thread, there is a discussion of a one-sided weld and issues presented by this procedure. The discussion has yet to produce a viable solution in our situation and without access, the backing cannot be removed. Therefore a one-sided weld is not allowed by the Bridge Welding Code. In addition, PJPs are also prohibited by AASHTO. As a possible solution, access holes for construction of the box are possible. With the access holes other problems arise. The access holes are in a very tight location on an internal plate of the box.
The 2” vertical plates of the structure are approximately 6’ tall and only about 1’-10” apart.
The access holes are in 2” and greater plate. We are investigating several questions. First, we do not have a large space and the access hole or slot can only be 12 wide or so and up to about 40 inches long. Does anyone have experience with removing backing bars through access holes? If so, what size and shape recommendations are suggested?
By SAP analysis, the placement of the holes creates increased and excessive stresses elsewhere in the structure. Therefore, we are looking for a way to structurally seal the holes while meeting the requirements of D1.5. Any suggestions would be appreciated!
The 2” vertical plates of the structure are approximately 6’ tall and only about 1’-10” apart.
The access holes are in 2” and greater plate. We are investigating several questions. First, we do not have a large space and the access hole or slot can only be 12 wide or so and up to about 40 inches long. Does anyone have experience with removing backing bars through access holes? If so, what size and shape recommendations are suggested?
By SAP analysis, the placement of the holes creates increased and excessive stresses elsewhere in the structure. Therefore, we are looking for a way to structurally seal the holes while meeting the requirements of D1.5. Any suggestions would be appreciated!