coachdave7
Structural
- Sep 1, 2012
- 2
Designed a beam for a house to help support the wood floor trusses. A W12x35 runs the length of the house in two sections, with one end of each section connecting to the foundation and the other end connecting to the flange of a W12x22. Now, after installation, he is going through with the HVAC installation. He wants to run it through the web of the W12x22 by cutting out the middle 8" of the web for 12" on one side of the connection and 16" on the other side of the connection. The W12x22 spans 4'-7" (reduced from the 9'-0" from the original design). The W12x35 connects at the midspan of the W12x35.
Now, I determined the moment couple based on the new centroid locations of the reduced T-sections. I determined the allowable compression and shear in the reduced T-section. And according to my analysis, everything checks out that it would be OK to make this modification.
Am I missing something??? because I feel awfully hesitant to give him the green light.
Has anyone else done something like this???
Now, I determined the moment couple based on the new centroid locations of the reduced T-sections. I determined the allowable compression and shear in the reduced T-section. And according to my analysis, everything checks out that it would be OK to make this modification.
Am I missing something??? because I feel awfully hesitant to give him the green light.
Has anyone else done something like this???