living2learn

Electrical
Jan 7, 2010
142
I am helping a facility out and noticed that they had a secondary spot network with the fault contribution around 75,000A symm. They have a homemade tap box (no ul listing, field fabricated with bus bars with very small standoffs). Does this box need a ul listing and be properly braced for the fault current it could recieve?
 
Replies continue below

Recommended for you

Which side of the meter is it on? It only needs a UL listing if someone makes one with a UL listing. When you start poking around in low voltage network vaults, you'll find lots of scary things.
 
It is the customers tap box located in their main electric room. It is where the utiltiy and customer meet. I stay very far away from utility vaults!
 
If the inspector didn't object, I would say it apparently did not require a UL label at the time it was installed. Is this 208 V? The fault current drops drastically as the distance from the transformer increases. I guess I wouldn't make an issue of it unless this is something you will be modifying. If this was an underrated circuit breaker, I'd approach it differently, but this may not even be a problem.
 
It is 480V and I am doing a building evaluation and thought this was worth mentioning. My logic for this critical site is if there is a large fault the tap box may explode.
 