H1 is the polarity side of the CT. Contrary to popular belief, the orientation of the CT in the circuit is immaterial, as the polarity marking gives relative polarity only. The secondary winding will most likely consist of evenly distributed turns around the core, with the taps being taken from completely distributed layers. The number of secondary turns will be 160/240/320, corresponding to the 800/1200/1600-5 taps.
The significance of polarity is that when instantaneous current flow is into the marked polarity side of the CT (H1 in this case), the instantaneous secondary current flow is out of the secondary polarity terminal. This determines the relative polarity for directionally sensitive devices connected to the CT secondary, and the trick is in connecting these correctly for the actual installed polarity.
As for the secondary terminals, these should be marked X1-X2-X3-X4, with the lower numbered terminal in use being the polarity terminal relative to the higher numbered terminal.
If the secondary terminals are not marked, then you will have to do a couple of tests to work them out, as follows -
- Do a secondary magnetizing current check on each pair of secondary leads in turn, with the primary open circuited - this determines the saturation voltage of the winding, which will be proportional to the number of turns. The terminals should correspond as follows - X1X4 = 320 turns; X2X4 = 240 turns; X3X4 = 160 turns; X1X2 = 80 turns; X2X3 = 80 turns
- Do a polarity test. This can be a "flick" test, where a DC ammeter is connected to the secondary terminals and a battery is used to energize the primary momentarily. By observing the direction of the ammeter deflection when the supply is put on and removed gives the relative polarity of the winding.