There are no codes to guide demagnetising of a saturated CT core, to my knowledge. CT manufacturer's should be able to provide you a write up, though. A couple of suggestions are,
A CT left idle for some time gets demagnetised (without doing any thing in particular).
Trace the Hysteresis curve of the CT core starting with its knee point voltage and then repeating the same several times, reducing the peak applied voltage little by little every time. This method id used if CT needs to be demagnetised in a short time and put back in service.