To all contributors,
Good knowledge base ......
To Elhouni,
With all due respect, I think you should state what it is you are attempting to acheive. The data from the CT Manufacturer should be all you need, unless you are trying to incorparate this CT into a bus voltage differential application, where all the CT's must be of matched impedances, otherwise it would be a standard overcurrent application ....
Having said that here is a possible way of figuring out the impedance/resistance of a CT.
Get yourself a current source (power supply, hopefully with a digital display, wired to supply current)
Hook up your CT to the power supply and adjust to a preferred current value i.e. 1 Amp, 5 Amps, etc
Take the voltage reading off the power supply or use a meter.
You now have currrent, voltage ... from this you can calculate the total resistance/impedance ... this will include the power supply internal resistance ...
To get the power supply internal resistance, you get a known resistance (hopefully a 1% resistor), do the same as with the CT. Once you get the total resistance, subtract the known resistance ... you now have the power supply internal resistance.
Substract the power supply internal resistance from the first resistance reading you got from the CT resistance/impedance setup ... you now have the CT resistance
This should do it .....
NOTE - this procedure is valid for both DC and AC therefore resistance/impedance.