111R
Electrical
- May 4, 2012
- 114
I'm attempting to fully understand CT operation and I'm getting stuck on a few seemingly simple concepts despite reading for quite a while. I realize this list is exhausting, so a few answers will still be helpful.
The excitation curve is a plot of secondary RMS exciting current vs secondary RMS exciting voltage.
1) I look at the accuracy classes of CTs and they are rated at C100, C200, C400, and C800. I found out that this means that a C800 CT can supply 800V into the secondary at 20x rated current (usually 5A*20=100A) within 10% accuracy. So, B1.0, B2.0, etc mean the same thing, but max burden impedance is given rather than secondary voltage. I am looking at PAGE 5 of the following PDF and I don't understand a few things:
Why is this a C400 CT? 486V is quoted as the secondary voltage at 10A. How is 486V within 10% accuracy? It's way beyond the knee point. And, why 10A...shouldn't it be at 100A (20*5)? I guess I don't really understand what the excitation curve indicates. The knee point voltage on this curve seems to be around 200V. What does the knee point tell us?
2) The knee point is where the core saturates, correct? So, the terms excitation curve and saturation curve are synonymous? What about magnetization curve?
3) Is the linear section before the knee point the desirable area to stay within for accurate current monitoring?
4) The IEEE30 and IEEE45 refer to the angles of a line tangent to the knee point. They indicate the knee point voltage of the CT. There is also IEC 10/50 which is the point where a 10% increase in exciting voltage causes a 50% increase in exciting current. Since I'm in the US, I doubt I will use IEC often. How do I select between IEEE30 and IEEE45? Why is there a need for two? IEEE30 will give a higher knee point value, but is there an application for one over the other?
Thanks for your time.
The excitation curve is a plot of secondary RMS exciting current vs secondary RMS exciting voltage.
1) I look at the accuracy classes of CTs and they are rated at C100, C200, C400, and C800. I found out that this means that a C800 CT can supply 800V into the secondary at 20x rated current (usually 5A*20=100A) within 10% accuracy. So, B1.0, B2.0, etc mean the same thing, but max burden impedance is given rather than secondary voltage. I am looking at PAGE 5 of the following PDF and I don't understand a few things:
Why is this a C400 CT? 486V is quoted as the secondary voltage at 10A. How is 486V within 10% accuracy? It's way beyond the knee point. And, why 10A...shouldn't it be at 100A (20*5)? I guess I don't really understand what the excitation curve indicates. The knee point voltage on this curve seems to be around 200V. What does the knee point tell us?
2) The knee point is where the core saturates, correct? So, the terms excitation curve and saturation curve are synonymous? What about magnetization curve?
3) Is the linear section before the knee point the desirable area to stay within for accurate current monitoring?
4) The IEEE30 and IEEE45 refer to the angles of a line tangent to the knee point. They indicate the knee point voltage of the CT. There is also IEC 10/50 which is the point where a 10% increase in exciting voltage causes a 50% increase in exciting current. Since I'm in the US, I doubt I will use IEC often. How do I select between IEEE30 and IEEE45? Why is there a need for two? IEEE30 will give a higher knee point value, but is there an application for one over the other?
Thanks for your time.