CT's are made safe by shorting them. Many have shorting hardware built into the terminals of the CT. Be very careful opening the shorting links if current is flowing in the primary conductor.
When the CT is shorted, the resistance is very low so the I2R is very low.
I lost a good meter on an open CT. Someone cut the leads in a wire bundle behind the control board. I was trying to locate a particular CT so I took a voltage reading across the relay and was behind the panel checking voltages across CTs looking for a match. (Yes, I admit it, I was trying to get lucky.)
I measured one CT and my meter made a buzzing sound and never worked again. After safeing the CT I found the leads cut in a bundle. I thanked God that I hadn't been running my hands near the cut ends following a conductor.
I was sure glad to go home that day.
The joys of working in the third world.
Bill
--------------------