rockman7892
Electrical
- Apr 7, 2008
- 1,178
I had mentioned in a previous thread that we have a utility transformer (4.16kV wye secondary) equipped with a tank ground CT that is picking up current during an external fault in our faciltiy. The transformer has a CT around a connection to ground on each side of the transformer (same direction) and the utility claims that each of these CT's is series connected at the relay so the currents cancel. (We proved wiring to relay is correct with currents canceling during normal operation)
Both myself and the utility are confused as to why we are seeing a tank ground current of aproximately 350A in the relay looking at these CT's during an external fault in our plant. Except for an internal winding faiure the only way I see these CT's current can add in the relay are if current is passing through each one of these CT's from ground and then exiting trhough the transformer pad as opposed to the other side of the tank where the opposite CT is located. Has anyone had similar experiences with tank ground CT's picking up on external ground faults or have any ideas what can be happening here? Should current even be flowing through these CT's during an external fault? (Possible low impedance path?)
Another issue that may or may not be related to this tank ground issue is the fact that the NGR inside the substation is somehow being shunted and allowing more than the design limited 400A of current to flow during a ground fault. We are trying to locate where this NGR may be shunted and see if this problem is related to the current being seen on the tank ground CT's.
Also during normal operation we notice about 10A of current on each of the tank ground CT's canceling in the relay to 0A. We also notice about 10A of current at the CT around the netural bushing of the transformer. Is this 10A of current considered normal during operation? We have a 3-wire system so the only place I can see it coming from is system charging current due to capacitive coupling.