JRLAKE
Mechanical
- Aug 2, 2006
- 145
We recently installed a 460V 250kW VSD air compressor (6 Pulse). The machine ran fine for a year. Lately the machine has been tripping the breaker. We also have had problems with other breakers within the same substation tripping. After ruling out mechanical issues we connected a power quality analyzer and recorded the following:
The only other equipment within the substation are four fixed speed 37kW boiler feed pumps. No lights. No computers. Nothing else.
The air compressor manufacturer says their compressor is not the source because it includes the appropriate filters. However when we turn the compressor off the tripping breaker problem goes away.
My questions are, do these filters fail and does anyone have an opinion on what is happening?


The only other equipment within the substation are four fixed speed 37kW boiler feed pumps. No lights. No computers. Nothing else.
The air compressor manufacturer says their compressor is not the source because it includes the appropriate filters. However when we turn the compressor off the tripping breaker problem goes away.
My questions are, do these filters fail and does anyone have an opinion on what is happening?