Hi, I have a problem.
I have a pump house at the end of a electric utility line out in the sticks. The utility drops the 14.4 kV single phase (only) to 240 v for distribution. We have a 50 kVA Xfmr to step up the voltage to 480 V. This is feed to a 75 HP Mitsubishi VFD which drives a 40 HP three phase pump.
Whenever the motor is operated at 60 Hz, the Xfmr blows its 200 amp fuses. We had the utility look at the power, and with their crap and the crap from the VFD converting single phase to three phase they measured current THD to be 24% RMS with 65% spikes (egad!), for voltage the values were 6.5% and 11%, and for the phase balance, etc it seems okay. Note that at 60 Hz the pump operates below FLA of 53.5 amp and at 460 V RMS.
I figure the transformer is too small because the drive is supposed to be over 93% efficient (1P to 3P) so the power to the VFD is about 45 kVA. With that distortion the dissipation within the Xfmr can drive the total load to over 50 kVA. So I want to put a 75 kVA in to handle the excessive current distortion. Is this thinking correct, or am I missing something? Thanks.....
I have a pump house at the end of a electric utility line out in the sticks. The utility drops the 14.4 kV single phase (only) to 240 v for distribution. We have a 50 kVA Xfmr to step up the voltage to 480 V. This is feed to a 75 HP Mitsubishi VFD which drives a 40 HP three phase pump.
Whenever the motor is operated at 60 Hz, the Xfmr blows its 200 amp fuses. We had the utility look at the power, and with their crap and the crap from the VFD converting single phase to three phase they measured current THD to be 24% RMS with 65% spikes (egad!), for voltage the values were 6.5% and 11%, and for the phase balance, etc it seems okay. Note that at 60 Hz the pump operates below FLA of 53.5 amp and at 460 V RMS.
I figure the transformer is too small because the drive is supposed to be over 93% efficient (1P to 3P) so the power to the VFD is about 45 kVA. With that distortion the dissipation within the Xfmr can drive the total load to over 50 kVA. So I want to put a 75 kVA in to handle the excessive current distortion. Is this thinking correct, or am I missing something? Thanks.....