I thank your ideas, are always helpful
7another4, I would like to give you more data in order to understand our situation. This specific project is a bit complicated and I will explain you why:
1) The largest fault current magnitude is on a low voltage transformer (at 460 V)
2) We are using this magnitude to size the conductor for the whole ground grid, however, according to our customer "idea" this current may flow only from the earthing point of the switchgear to the neutral of the transformer to "close the circuit".
As you can see, there are two grounding points, one at the switchgear and the seond at the transformer neutral (X0 terminal).
3) Then, this current is not causing the step and touch voltages because it is not flowing through earth.
The current magnitude that will flow through the grounding grid causing the step and touch voltages is at 4.16 kV and it is limited to 800 A by a resistor installed at the neutral of this transformer.
4) As you can see, the step and voltage potentials are not a problem, our only problem is the size of the conductor which may not tolerate a large current for a while without exceeding the 250 celsius degrees and all the side effects on connectors and so on.
5) Because of that, we have thought that determining the current distribution on the grounding grid could be an alternative to prove that the whole grounding grid will not be exposed to the large fault current, in fact using a commercial software (previously mentioned by one of the colleagues), we found that by injecting 53 kA into the down lead, this current is divided and the surrounding segments of the grounding grid to the injection point are taking 27 kA as a maximum, this magnitude will not shown a temperature over 250 C and of course connector neither.
But, we are not sure if this can be done despite being mentioned on IEEE Std 80-2000
I thank your feedback