Let's back up to Peterbs earlier post.
"- The generator is equipped with six (6) leads
- Three (3) leads are connected to one end of each phase winding and to the generator output terminals - call these A, B, C
- The other three (3) leads are connected to the other end of each phase of the generator winding - call these X, Y, Z
- The load is connected to leads A, B, C
- Leads X, Y, Z are connected together to form the generator star point
- The star point is connected to ground through a neutral grounding transformer
- Whatever current flows in lead A also flows in lead X, and correspondingly for B and Y, C and Z (this is the principle of generator differential protection)
- At the star point, the currents in leads X, Y and Z are added vectorially. If the system is balanced, the vector sum is zero, if the system is unbalanced or if there are triple-n harmonics present, the zero sequence or summated harmonic current will flow in the neutral connection "
Let's take an instantaneous look at B & C while A has gone to zero volts. Lets make B flow to C. We now have a path that goes B to the LOAD and back to C. Then C comes out at Z which is connected to Y and completes our little loop back to B. That's a series loop and a complete circuit. If 10 amps goes through the load and ... in a series circuit ALL the currents are EQUAL ... then that means 10 amps is flowing through Z & Y. Peterbs points out that Z &Y are part of the star point. So the answer is YES, current does go through the star point.
Show me how that answer is "no".
I don't want to hear theory that the exact calculated phaser center (your node) happens to be one molecule of wire in the star point and no current flows in that one molecule. Dakota just asked the simple question is there any current going through the star point. And when he asked that he was looking at wires ... not a single point calculated down to a point impossible to physically measure.
Now that I have said that I can see what your point is when you say no current is flowing. But, again put an ammeter on any of the three wires going to the star point and you will measure a current.
Dakota, maybe the correct answer is both. There is NO current through the EXACT calculated center of the star point but every other molecule of wire in the star point carries the rest of the current!
How does that sound?
SteveKW.