We have a 130kw submersible pump on a VSD that is showing nearly 9% currant imbalance. It also shows induced current on the earth rising from the motor.
The pump is 100m deep and the riser pipe is 8 inch and the well casing is 12 inch. Pump is 12 inch.
95 mm2 cable is run down to the 6 wire 130kw motor (three conductors up the riser, 6 out of motor).
Insualtion resistance starts @ 35mOhm and rises to 80mOhm
Winding resistance is .09 .09 .09 - so balanced.
From memory and would have to check , the DAR test was 1.1
We have tried all three hook ups and the imbalance follows the blue phase in each hookup.
Amps
212 185 208
voltage
r-w w-b b-r
449 450 444
Earth currant is 26a (3.5V) when connected to the well head imbalance is there, when disconnected imbalance is still there.
Any ideas on what is happening and how to fix?
Cheers
N
The pump is 100m deep and the riser pipe is 8 inch and the well casing is 12 inch. Pump is 12 inch.
95 mm2 cable is run down to the 6 wire 130kw motor (three conductors up the riser, 6 out of motor).
Insualtion resistance starts @ 35mOhm and rises to 80mOhm
Winding resistance is .09 .09 .09 - so balanced.
From memory and would have to check , the DAR test was 1.1
We have tried all three hook ups and the imbalance follows the blue phase in each hookup.
Amps
212 185 208
voltage
r-w w-b b-r
449 450 444
Earth currant is 26a (3.5V) when connected to the well head imbalance is there, when disconnected imbalance is still there.
Any ideas on what is happening and how to fix?
Cheers
N