I am using a power analyzer to monitor a 480V wye system. I have both CT's and Voltage inputs that come with the monitor which I will connect to the equipment. Because of the access to the service I am going to hook the CT's directly around the secondary of CT's and hook the voltage leads to the secondary of PT's.
My question is, the PT's are a 480:120V ration arranged in a corner grounded open delta arrangement. I was concerned that if I hooked up the PT's and CT's as described above then I might get false power readings because of a possible phase shift or wrond phase angle resulting from using the open delta PT arrangment.
Because the CT's are direclty on the wye system, I would think that thier phase angles would be referenced L-N. The PT's would have thier phase anlges referenced at L-L angles therefore the voltage phasors would be:
V a-b = 480V @ -330deg
V b-c = 480V @ -90deg
V c-a = 480V @ -210deg
Would this 30deg phase shift from L-N to L-L phase angles for the voltage give false current readings since the currents would be referenced at L-N angles?
To use the meter to monitor PT's you have to set it up for a delta system configuration and I was concerned about false readings as described above.
My question is, the PT's are a 480:120V ration arranged in a corner grounded open delta arrangement. I was concerned that if I hooked up the PT's and CT's as described above then I might get false power readings because of a possible phase shift or wrond phase angle resulting from using the open delta PT arrangment.
Because the CT's are direclty on the wye system, I would think that thier phase angles would be referenced L-N. The PT's would have thier phase anlges referenced at L-L angles therefore the voltage phasors would be:
V a-b = 480V @ -330deg
V b-c = 480V @ -90deg
V c-a = 480V @ -210deg
Would this 30deg phase shift from L-N to L-L phase angles for the voltage give false current readings since the currents would be referenced at L-N angles?
To use the meter to monitor PT's you have to set it up for a delta system configuration and I was concerned about false readings as described above.