This is the designation for current transformer per IEC Standard 185 as follow:
“10”…………….Declare composite error at accuracy limit primary current (Ex 2.5 & 10)
“P”………………Indicates the CT classification (Ex. P=Protection, M=Metering, TP)
“15”……………..Rated secondary reference voltage (Ex. 10,15,20, 30, 75).
The rate accuracy factor other than 20 should be indicated in the designation.
NOTE: There is an equivalence ANSI designation (Ex C100 to C800)